wells...
wells...
Just to point out that some submersible pumps including constant velocity type have the starting and run caps in a control panel that many times is located remotely most of the time at the pressure tank, without disconnecting all these conductors you would still have voltage on the motor, this is also in the exception of 430.102
also its not wise to disconnect a motor from a VFD while the VFD is energized, another reason to allow the disconnect before the VFD.
Hi Wayne,
Normally I would agree with what you are pointing out, but 430.102 I believe is generally applicable to commercial-industrial installations using 3 ph, 600V+ and VFD's. ( Of the many domestic well systems I have set, only one was a 3ph configuration that would apply here.) All that I am familiar with were rural installations that utilized a 2-wire feed of a long distance from a well head to a barn or residence. Usually a captive pressure tank is located at the structure inside or at an attached shed. (re: water line friction and static level drop is less distance to outlets in the structure)
The two wire feed requires that the pressure switch be within 48" of the pressure tank to eliminate re-occurring surge cycling. In most cases a long distance 2-wire direct burial is fed to a remote wellhead that has a motor controller mounted to it for a 3-wire non-cap deep submersible that is of a higher hp rating. (re: usually 2.0 hp or larger)
Most residential using deep submersibles are 2-wire 240V, 1 ph feeds, and generally a 0.5 to 1.5 hp pump well supply unless agricultural use is of size significance from a single unit. (depending on the supply GPM and draw-down) I would sell the client on a small well house or in-ground sealed container (w/lock) for remote locations that kept livestock and farmers from running over an exposed head. In most cases, the lock gets lost and the enclosure becomes accessible. (i.e. In hunting season, poachers break-in for water refill access.)
Please understand, there are situations where safety can be improved for modern well systems exposure. If any proposal is to be made, I would include deep submersible well systems as an addition to Article 680 and 682 installation sections. (682.14 update?) I agree with Dennis that domestic well systems have been overlooked for wiring methods in rural and agricultural safety.