An existing pool has a Club House and Pump House. The Main PB is in the Club House(150ft from Pump House). 225A, 208/120Y, 42ckt Main Panel. A 100A 3? breaker w/#8THW 4wire feeds the Pump House 100A Panel. 9ckts are used in the Pump House Panel.
1. Shouldn't there be a disconnecting means for the pump house somewhere at the pump house. 6breaker rule is already exceeded.
2. Is there a "gimmee" on pool equipment buildings that I'm missing? (searched the code)
3.Does the breaker at the club house act as the disconnecting means for the pump house. BTW, the panel is 42ckt(mostly full), top-fed, 225 amp.
There's plenty of capacity in the system except for the #8awg carrying 67amps, but no disconnect for the pump house.
Need guidance.
1. Shouldn't there be a disconnecting means for the pump house somewhere at the pump house. 6breaker rule is already exceeded.
2. Is there a "gimmee" on pool equipment buildings that I'm missing? (searched the code)
3.Does the breaker at the club house act as the disconnecting means for the pump house. BTW, the panel is 42ckt(mostly full), top-fed, 225 amp.
There's plenty of capacity in the system except for the #8awg carrying 67amps, but no disconnect for the pump house.
Need guidance.