We have a sewage pump station 600' from the building. It requires 60A 208V 3 phase only, no neutral is needed, the pump panel has 2 breakers in it for the pumps and 1 for the control power transformer. There is a permanently installed Generator at the pump station. The engineer is requiring 3 phases, a full size neutral (2/0 for voltage drop), and a ground wire from the building to the transfer sw next to the pump panel. He is also calling for a four pole transfer switch. We have not seen this before, typically 3 phases and a ground wire are run to these. Can anyone explain where the neutral requirements for this is in the code. If this is for a grounding electrode conductor can it be sized per 250.66 (#4 for 2/0 SE conductor)?
If we have to have this 2/0 neutral is a ground wire still required? And if this is required on this set up why it is not used on outside condensing units, chillers or similar equipment.
If we have to have this 2/0 neutral is a ground wire still required? And if this is required on this set up why it is not used on outside condensing units, chillers or similar equipment.