Bidding on existing pump station project that requires changing out overhead service with new underground service and changing out existing switchboard. The loads are 3(Ea) 335 HP pumps(249.91KVA each), 2(Ea) panelboards(186.1KVA) for total of 935.83KVA or 749KW.
The problem is that there is an existing 650KVA(520KW) standby generator with ATS feeding entire load. Not sure that all pumps will ever run at same time or not. What is proper way to calculate load? I'm thinking NEC 08, 702.5(2)(a) will dictate resizing existing generator. Any thoughts? I also posted this topic in the electrical calculations/engineering forum.
The problem is that there is an existing 650KVA(520KW) standby generator with ATS feeding entire load. Not sure that all pumps will ever run at same time or not. What is proper way to calculate load? I'm thinking NEC 08, 702.5(2)(a) will dictate resizing existing generator. Any thoughts? I also posted this topic in the electrical calculations/engineering forum.