I'm a Canadian familiarizing myself with NEC.
Currently working on a project that will be installed in a Class I Div 2 area. I have an large enclosure I'll be entering with cable and conduit from a Class I Div 2 area exterior to the enclosure, whereas the enclosure itself will be purged to allow a GP area class. Reading through 501.15 2 Pressurized Enclosures, am I correct in interpreting that I will need conduit seals packed and poured (ie: crouse EYS type) for rigid conduit, and sealed cable glands (ie: T&B STX) for MC-HL?
If this is my correct interpretation, will the seals be required to be installed on the exterior of enclosure in the Div 2 area? or would they be permitted to be install just on the inside wall of the purged enclosure?
Any guidance would be greatly appreciated!
Currently working on a project that will be installed in a Class I Div 2 area. I have an large enclosure I'll be entering with cable and conduit from a Class I Div 2 area exterior to the enclosure, whereas the enclosure itself will be purged to allow a GP area class. Reading through 501.15 2 Pressurized Enclosures, am I correct in interpreting that I will need conduit seals packed and poured (ie: crouse EYS type) for rigid conduit, and sealed cable glands (ie: T&B STX) for MC-HL?