I'm having a debate with our engimneering group on what push buttons to use on a purged panel in a class 1 div 2 area. The purge I think is a Z purge (alarm only). I contend a stanadard pushbutton is OK, engineering says I have to use explosion proof. What say you?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The arc producing contacts are inside of the purged enclosure. As long as you can maintain the required purge flow and or pressure, I see no need for explosion proof pushbuttons.
 