Purging enclosures for Class 1 Div 1

Status
Not open for further replies.

Designguy

New member
I used to design enclosures for class 1 Div 2 environments, due to 110V, 15 amp and (potential for) pyrophoric gases we would use a nitrogen purge of enclosure to fulfill the requirements of the code. Can this mitigation strategy work in a class 1 Div 1 environment that has a potential for gasoline vapors to be trapped?

Thanks all
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Typically, pyrophoric materials do not require electrical equipment mitigation. See NEC Section 500.5(A).

That being said, the protection technique of purging/pressurizing may indeed be applied to Division 1 installations. It is similar, but not identical, to Division 2 applications.

NFPA 496 recognizes 3 basic methods of purging/pressurizing. Two of them (Types X and Y) apply to Division 1 situations. Without knowing the details of your application Chapters 1 through 5 would seem to apply.
 