I was listening in on a CMP 17 task group meeting today, and part of the discussion was about the effectiveness of the single ring wire for perimeter bonding, and the comments were, with a bonding system compliant with 680.26, there have been no reported incidents involving a shock between the bonded pool water or equipment and the surrounding deck. There have been a number of cases of injury and even death where the perimeter bonding had not been installed.
That being said, if there was some kind of event that caused a high current to flow though the bonding system there could be excessive voltage drop across the bonding system creating a shock potential.
I don't think elevated voltage, without current is a real problem. Mike Holt has a video of him in an energized pool, and even with 100,000 ohm resistor in the bonding conductor to some of the parts there was not a touch potential between the parts.
Take a look at about one hour and 30 minutes into this video that Mike did:
www.mikeholt.com/pools
Note that I am not aware of what type of bonding system was used in the pool in the video.