I am familiar with explosion proof pushbuttons and enclosures, but I am very unclear about pressurized enclosures!! Are standard pushbuttons permitted in a pressurized enclosure, with approved monitoring, in Class II Div 1?
For Class II installations, you probably have no need of a pruged or pressurized enclosure. Standard pushbuttons are permitted in "dust-ignitionproof" enclosures.
If you are really asking about a Class I, Division 1 location, then, yes you can use standard pushbuttons in a pressurized enclosure, but you need more than just monitoring to change from Division 1 to non-hazardous. You need to have a an automatic disconnect of the power to the pressurized enclosure on loss of pressure. This relay or contactor will have to be in an explosionproof enclosure or installed in a non-classified area.
Thank you, Don. The installation is in China; the Local Design Institute is a bit anal about combustible dust; they have their own Zone Classification which is loosely based on other standards groups. I would just like to be able to point to documentation of this permission in NFPA. I can't find it in NFPA 70; is this (non-rated pushbuttons, etc.) specified in NFPA 496, would you know? Thanks again!
I would just like to be able to point out the documentation of this permission (non-rated pushbuttons, etc.) in NFPA. I can't find it in NFPA 70; is this specified in NFPA 496? Would anyone be able to answer this question?
Another vendor told me it was not permitted!
Thanks again!
The NEC only requires that the enclosure for a push button or other type of switch be dust tight.
502.115(B) Class II, Division 2 In Class II, Division 2 locations, enclosures for fuses, switches, circuit breakers, and motor controllers, including pushbuttons, relays, and similar devices, shall be dusttight.