am replacing a pushmatic panel at the request of client could not see what the amperage was my question(S) are ......first are all pushmatic panels 100 amp and where to find that info on it ........second can it b replaced with a regulatory 100 amp service any guidance would b most appreciated .......new2electricity :?
 
investigate

investigate

check to see what size wires are feeding it now?
is this residential or commercial?
it sounds like resi- if it is then just pull in new #4 conductors from the meter socket to the new panel.
 
I have seen 200 amp panels that have 2 separate sets of buses and a 100 amp main supplying each set.<BR><BR>I don't ever recall seeing a 200 amp main breaker panel. <BR><BR>I seem to recall someone posting a picture of a three phase panel at some time, may have to try to find it.
 
I have seen 200 amp panels that have 2 separate sets of buses and a 100 amp main supplying each set.<BR><BR>I don't ever recall seeing a 200 amp main breaker panel. <BR><BR>I seem to recall someone posting a picture of a three phase panel at some time, may have to try to find it.

Like this one.
 

Attachments

  • Picture130.jpg
    Picture130.jpg
    124.6 KB · Views: 1
Like this one.

[img[http://forums.mikeholt.com/attachment.php?attachmentid=6182&stc=1&d=1325501542[/img]


That is a 2 gang "all in one" w/ 2- 100A distribution sections. (It's my photo,LOL). ITE Pushmatics were made in 200A models using either a QJ or a QP frame breaker as a main depending on the age of the panel on main breaker* models, they were also avail. in 3? models too.....

* 2-100A Pushmatic mains were also avail. wish my scanner worked, could have put up a scan from a 1973 ITE Imperial Corp. catalog.
 
are all pushmatic panels 100 amp and where to find that info on it ........second can it b replaced with a regulatory 100 amp service any guidance would b most appreciated
Welcome to the Forum.

A lot of Pushmatic panels were installed in the decades when the "split bus" design was very popular. This, in many ways, was a cost containment tactic developed as the required minimum service size was changed from 60 A to 100 A. The 100 A main breaker came at a premium price, compared to the commodity 15 - 60 A breakers prices.

The Split Bus panel has positions for up to six service disconnects. One is used to power the second section of the panel, the "Lighting Section", where most of the general lighting and small appliance circuits are located. Large double pole loads, such as the electric range, electric clothes dryer, electric water heater, central air, etc., would be installed in the "Service Disconnect" section.

The size of the service entrance conductors was determined by the calculation for the dwelling, plus whatever additional size the installer wanted to add above that minimum.

Upshot: If your client's panel is a Split Bus, no breaker or label on the panel will indicate the rated service entrance ampacity. One has to know the service entrance conductor guage and insulation class and date of Code that the installation was under to be able to look up the rated ampacity.

I've seen a lot of 125 Amp services over the years, in my geographic area, in the guise of a panel, that at first glance, appeared to be main lugs only, but upon closer examination had up to six service disconnects, none larger than 60 Amps.
 