Good morning
Have a job that is to start Friday once the poco pulls the meter. This is the result of a house closing and issues written up by the buyers home inspector. My employer has been hired to inspect, repair or replace these issues.
I've looked at the job and would like some input to some questions I have. We will be dealing with an old pushmatic Electri-Center (100 amp) using these type breakers
http://www.aplussupply.com/break/push/push.htm
This is the first time I have been in a panel like this. It is split buss. The bottom half of the panel is the lighting section and is controlled by a 50 amp breaker in the top half. The top half of course are main disconnects to 240 olt loads like the range.
I found this thread while researching this type panel so I could shorten my learning curve having not dealt with one of these panels.
http://forums.mikeholt.com/showthread.php?t=66644&highlight=pushmatic+breakers
A reply by noxx that these breakers will not trip on over current...only overload...has me concerned. So I hope my coming question is not to trivial.
The house is wired with no grounding non-metallic romex all going to the pushmatic. A MLO GE 100 amp sub-panel has been added in 1998 fed from a 60 amp breaker in the upper half of the pushmatic. It is a #2 awg seu al cable feeder. All wiring out of the GE sub is modern nm-b.
So two questions (for now).
1.) The range branch circuit is a older cloth sheathed al seu #8.. 3 wire, however it was cut and spliced in a jb to 10/3 nm-b copper using regular wirenuts. OCPD is a pushmatic 40 amp. So question....It is a very simple run from either panel so will replace with a 4 wire #8 copper cable probably nm-b. The new range that was recently installed is 10.7KW.
If these pushmatics only trip on thermal overload is it going to serve any purpose to run a four wire to the pushmatic?
I'm thinking run to the new GE sub-panel if this is the case. Demand load is small only split system central air and gas heat. Ge panel is feeding all the kitchen lights and kitchen receptacles from a new remodel in the late 90's several spaces are open.
2.) The A/c is newer but is also DIY as was the deal with the range branch circuit. The branch circuit is 10/2 G copper nm-b but they cut the ground off just outside the pushmatic panel clamp as the outer sheath does not go into the clamp. No place to put the ground I guess as the neutral buss is full. Anyway question....
Are these pushmatics HACR rated? I would assume they are not.... age dating before we rated breakers for hacr. I don't see a listing on the breaker but really can't read anything on them. No issues with the A/C as per owners statement using the pushmatic.
If not then we have to move this to the ge sub panel? I have read UL 489 and it seems just about any modern breaker is now acceptable for HACR applications whether listed as such or not....maybe misinterpreting what I see there but only way I can positively get Hacr is from the new GE.
Now, if so, I have a 40 amp range branch circuit and a a/c on the feeder to the sub and all of the kitchen, choosing that as an option. I haven't looked at the A/c nameplate yet but is a small home less than 1000 sq. ft. so unless the homeowner did some godzilla condenser unit I should be looking at a min. circuit ampacity in the 20's. They have the a/c 10/2 G on a 50 amp pushmatic breaker. Playing with the options to move the range and a/c loads to the sub and upsizing the ocpd and feeder ampacity due to the 60c terminations in the pushmatic seems to get a little goofy in design. Yes ... I know the feeder needs to be 4 wire.
Comments please
EDIT: A panel replacement or service upgrade is not going to happen, unless buyers agree to pay for it. We have already ran that by the seller.
Stubbie
Have a job that is to start Friday once the poco pulls the meter. This is the result of a house closing and issues written up by the buyers home inspector. My employer has been hired to inspect, repair or replace these issues.
I've looked at the job and would like some input to some questions I have. We will be dealing with an old pushmatic Electri-Center (100 amp) using these type breakers
http://www.aplussupply.com/break/push/push.htm
This is the first time I have been in a panel like this. It is split buss. The bottom half of the panel is the lighting section and is controlled by a 50 amp breaker in the top half. The top half of course are main disconnects to 240 olt loads like the range.
I found this thread while researching this type panel so I could shorten my learning curve having not dealt with one of these panels.
http://forums.mikeholt.com/showthread.php?t=66644&highlight=pushmatic+breakers
A reply by noxx that these breakers will not trip on over current...only overload...has me concerned. So I hope my coming question is not to trivial.
The house is wired with no grounding non-metallic romex all going to the pushmatic. A MLO GE 100 amp sub-panel has been added in 1998 fed from a 60 amp breaker in the upper half of the pushmatic. It is a #2 awg seu al cable feeder. All wiring out of the GE sub is modern nm-b.
So two questions (for now).
1.) The range branch circuit is a older cloth sheathed al seu #8.. 3 wire, however it was cut and spliced in a jb to 10/3 nm-b copper using regular wirenuts. OCPD is a pushmatic 40 amp. So question....It is a very simple run from either panel so will replace with a 4 wire #8 copper cable probably nm-b. The new range that was recently installed is 10.7KW.
If these pushmatics only trip on thermal overload is it going to serve any purpose to run a four wire to the pushmatic?
I'm thinking run to the new GE sub-panel if this is the case. Demand load is small only split system central air and gas heat. Ge panel is feeding all the kitchen lights and kitchen receptacles from a new remodel in the late 90's several spaces are open.
2.) The A/c is newer but is also DIY as was the deal with the range branch circuit. The branch circuit is 10/2 G copper nm-b but they cut the ground off just outside the pushmatic panel clamp as the outer sheath does not go into the clamp. No place to put the ground I guess as the neutral buss is full. Anyway question....
Are these pushmatics HACR rated? I would assume they are not.... age dating before we rated breakers for hacr. I don't see a listing on the breaker but really can't read anything on them. No issues with the A/C as per owners statement using the pushmatic.
If not then we have to move this to the ge sub panel? I have read UL 489 and it seems just about any modern breaker is now acceptable for HACR applications whether listed as such or not....maybe misinterpreting what I see there but only way I can positively get Hacr is from the new GE.
Now, if so, I have a 40 amp range branch circuit and a a/c on the feeder to the sub and all of the kitchen, choosing that as an option. I haven't looked at the A/c nameplate yet but is a small home less than 1000 sq. ft. so unless the homeowner did some godzilla condenser unit I should be looking at a min. circuit ampacity in the 20's. They have the a/c 10/2 G on a 50 amp pushmatic breaker. Playing with the options to move the range and a/c loads to the sub and upsizing the ocpd and feeder ampacity due to the 60c terminations in the pushmatic seems to get a little goofy in design. Yes ... I know the feeder needs to be 4 wire.
Comments please
EDIT: A panel replacement or service upgrade is not going to happen, unless buyers agree to pay for it. We have already ran that by the seller.
Stubbie