PV 30 amp breaker on extreme opposite position of main 200 amp breaker question

Status
Not open for further replies.

Anthony384b

New User
Location
Tracy, CA
Occupation
Retired from Electronics Field
Hello,

Based on my read of 705.12(D)(2)(3)(b), my 30 amp 2 pole PV breaker must remain at the extreme opposite end of my 200 amp main breaker. Therefore, in the strictest sense, I could not replace my 30 amp PV 2 pole breaker with a 30 amp center connected quad breaker to make extrq space because a 15 amp or 20 amp (non-PV related) breaker would then occupy the extreme opposite position on my 200 amp rated bus bar referenced to the main 200’amp breaker.
Correct?

Thank You, Anthony
 