What effects can a PV array have on a back up generator? I'm thinking in terms of performance and load balance.
What effects can a PV array have on a back up generator? I'm thinking in terms of performance and load balance.
What effects can a PV array have on a back up generator? I'm thinking in terms of performance and load balance.
If it is a grid tied array .
So, it is a grid tied PV tied to a utility, with a transfer switch to a gen? The PV is connected to the load side of the transfer switch?Yes once the utility goes the inverter kicks out, but once the gen is up and running, the inverter would see a signal again and turn back on correct?
That is an interesting gen. I don't think I have ever seen a 200kw single phase gen. Hummm. Probably is a 300kw, 12 lead. So the driver is likely 500hp.The system is an 800A, 240V, single phase. The generator backs up the entire facility.
We don't know the size of the proposed PV array, nor anything about the proposed controls - so there is no way to even guess.The client wishes to add a PV array to backfeed into the system. I'm wondering if there could be sufficient oscillation in the system from the PV array changing it's current output (and if it would happen fast enough) to prematurely wear out the generator.
You may well need an isolation switch, but with the limited information we have, I would not tend to base the decision on gen longevity. I would guess that a 500hp driver is going to be hard to jerk around to the point of damage. As for backfeed/reverse power damage, that is what protective relays are for.Current thinking on the design end for this is that an isolation switch is warranted to protect the longevity of the generator. .
We don't know who (or what) is (are) your "design end" - don't know her capabilities, knowledge, or resources. And , of course, we don't have any design specs. So from here, the best I could suggest is controllable micro inverters. That way the controls could switch the PV out in stages to keep a minimum load on the gen.A potential problem exists if the load is less than the PV output, since the generator unlike the grid cant readily absorb power, it can only supply power.
Holy weasel words, Batman! I can't believe we escaped the harmonic buildup vortex generator.:grin:And after talking to another engineer at work, an isolation switch is being put in to prevent harmonic buildup from happening.