2017 NEC 690.9(B)(1) "Not less than 125 percent of the maximum currents calculated in 690.8(A)."
Why must the fuses used be NOT LESS than 156% of Isc rather than NOT MORE than 156% of Isc?
In every other situation I can think of, the purpose of OCPD is to protect the conductors and/or other equipment. I understand that the current produced by a string can exceed the STC Isc when in the field. But what other reasons are there for setting a minimum fuse size?
Is there a maximum fuse size requirement that also applies? I do not expect using a 100A fuse on 10A strings using 10AWG CU would be to code, but where in the text is the maximum fuse size capped for DC source circuits?