this is really getting to me. One interpertation of the code is invalidated by another. we should have the AHJ write the book!
So
PV Disco located at nearest point of entrance of PV DC system conductors is considered "Accessable" even if behing a locked door. Correct? (110.26 (G))
PV system conductors ( over 100Voc under 600)may be in PVC conduit if PV DC disco is "... nearest point of entrance of system (DC) conductors" 690.14(C)(1)
690.31 (E) states that if Disco is remote (does that mean out of site of from point of entrance and Inverter?) conductors must be in metal conduit.
Help, please!! I dont want to have to start installing a $200 sw and more wire when , according to John Wiles the FD has a key to every lock in the country! (fire ax)
How many elect utiltuy rooms with inverters in them are locked? Most? or few?
So
PV Disco located at nearest point of entrance of PV DC system conductors is considered "Accessable" even if behing a locked door. Correct? (110.26 (G))
PV system conductors ( over 100Voc under 600)may be in PVC conduit if PV DC disco is "... nearest point of entrance of system (DC) conductors" 690.14(C)(1)
690.31 (E) states that if Disco is remote (does that mean out of site of from point of entrance and Inverter?) conductors must be in metal conduit.
Help, please!! I dont want to have to start installing a $200 sw and more wire when , according to John Wiles the FD has a key to every lock in the country! (fire ax)
How many elect utiltuy rooms with inverters in them are locked? Most? or few?