I'm working on a grid-tied ground mount solar project that has three separate arrays of 12 modules each, which are somewhat spread out on the property. The system uses microinverters (APSystems DS3-L) so two solar modules plug into each microinverter, and from there its AC all the way back to the utility.
All three ground mount arrays have 4-space loadcenters that act as combiners with 2 breakers protecting three microinverters each using 12AWG trunk cables. From each array loadcenter, 6AWG runs in buried conduit back to a central load center that combines all three arrays into a single home run feed, and also houses the PV disconnect breaker and solar generation meter.
Each array has its own 10AWG EGC, and all three tie together in the central PV load center. This central PV load enter is fed from the residence using a 4-wire MHF in conduit with a 4AWG ground that ties back to the single neutral-ground bond in the home's main load center.
My question is about ground rods. We plan to install the standard two 8' ground rods at the central PV load center, which is mounted to the first array. This first array is about 100' from the residence. This takes care of re-establishing the GEC away from the residence.
For the other two arrays, which are about 70' and 100' from the first, should I place ground rods at each of these arrays also? Or maybe one on each? Or should I just consider the EGC's from the central PV loadcenter to be a sufficient ground? Doing this would make it a single-point ground back at the central PV loadcenter.
My initial thought is that at least one ground rod at each array would provide the best protection.
But I'm also concerned about creating ground loops by tying together multiple ground rods and array frames...so that's why I'm asking.
I'd appreciate your thoughts on this....Thanks!
All three ground mount arrays have 4-space loadcenters that act as combiners with 2 breakers protecting three microinverters each using 12AWG trunk cables. From each array loadcenter, 6AWG runs in buried conduit back to a central load center that combines all three arrays into a single home run feed, and also houses the PV disconnect breaker and solar generation meter.
Each array has its own 10AWG EGC, and all three tie together in the central PV load center. This central PV load enter is fed from the residence using a 4-wire MHF in conduit with a 4AWG ground that ties back to the single neutral-ground bond in the home's main load center.
My question is about ground rods. We plan to install the standard two 8' ground rods at the central PV load center, which is mounted to the first array. This first array is about 100' from the residence. This takes care of re-establishing the GEC away from the residence.
For the other two arrays, which are about 70' and 100' from the first, should I place ground rods at each of these arrays also? Or maybe one on each? Or should I just consider the EGC's from the central PV loadcenter to be a sufficient ground? Doing this would make it a single-point ground back at the central PV loadcenter.
My initial thought is that at least one ground rod at each array would provide the best protection.
But I'm also concerned about creating ground loops by tying together multiple ground rods and array frames...so that's why I'm asking.
I'd appreciate your thoughts on this....Thanks!