Anyone have any experience in connecting solar into a panel with a GFI main? 2011 705.30(3) says it has to be connected on line side. There is an exception that it can be connected on load side if GFI protection will still work. In my situation I can't attach on line side because it has cold sequence cts and the main is upstream from the cts. I have to connect behind the metering. I am not sure that the GFI protection would work if the load on the building is small and the system is exporting a lot of power. This is because the inverter would be sourcing the fault current and it would not go through the neutral ct. It would work on a low impedence fault but not reliably if there were impedence in the fault limiting the current. I have seen this done many times but I don't think it meets code. Any ideas?