JimWyatt

Member
Location
Glendale, AZ
I am building a PV System that is going to have 2x 32 amp inverters feeding my electric panel. My utility company show examples of a load side tap. Since I would not be tying to the load side bus work, would I still have to adhere to the 120% bus feed rule?
LOAD TAP3.jpg
 
I am building a PV System that is going to have 2x 32 amp inverters feeding my electric panel. My utility company show examples of a load side tap. Since I would not be tying to the load side bus work, would I still have to adhere to the 120% bus feed rule?
View attachment 2554337
Let me pull this one. Deeper research and Load tapping doesn't buy me anything but breaker space on the panel. Bus still isn't over current protected
 
Yes, if you tap conductors feeding an MLO panel then the conductors are just an extension of the panel bus.
 