I started delving into sizing batteries this past week, and have these questions (based on the diagrams in Figure 690.1(b) in the 2017 NEC, showing all the main components of solar PV and battery / energy storage systems):
1. For Stand-alone systems, where you just have the solar pv array and the batteries (and the charge controller), the pv array voltage should exceed the battery bank voltage only by about 20% - 30%, correct? For example, if your battery bank is 24 volts DC, you cannot have a solar pv array at 400V-600VDC as you would in a regular interactive system with no batteries, for a residence?
2. For AC Coupled Multimode systems, here you CAN have the solar pv array voltage at 400-600VDC for a residence, correct? It seems like this would work, since the output of the interactive inverter is at 120/208 or 120/240 volts, which then goes into a multimode inverter and brings the voltage down to 24 volts DC, to charge the battery. (or whatever the battery bank voltage is).
Thanks again.
1. For Stand-alone systems, where you just have the solar pv array and the batteries (and the charge controller), the pv array voltage should exceed the battery bank voltage only by about 20% - 30%, correct? For example, if your battery bank is 24 volts DC, you cannot have a solar pv array at 400V-600VDC as you would in a regular interactive system with no batteries, for a residence?
2. For AC Coupled Multimode systems, here you CAN have the solar pv array voltage at 400-600VDC for a residence, correct? It seems like this would work, since the output of the interactive inverter is at 120/208 or 120/240 volts, which then goes into a multimode inverter and brings the voltage down to 24 volts DC, to charge the battery. (or whatever the battery bank voltage is).
Thanks again.