Paul-tecnico
- Milan, italy
I?m an Italian electrical designer and i have a doubt about the fuses for the protection of 2 strings in parallel for a photovoltaic plant in USA.
The following table shows the system configuration:
The size of these fuses is determined by the maximum circuit current output (Imax) = 1.25xIsctot
Imax=(Isc1+Isc2)x1.25=(8.95A+8.95A)x1.25=22.375A
In fuse=Imax x 1.25=27.97A
So I chose fuses with In=30A.
The fuse nameplate ampere ratings, for the PV modules is 15A.
Based on NEC 110.3(B) we are required to use the module as it was listed. This prohibits us from using a larger fuse (first problem).
Also, NEC 690.8(D) gives us a requirement for sizing module interconnection conductors of paralleled strings. Ampacity needs to be greater than [(n-1)*Isc*1.25]+Series Fuse Rating where n=number of parallel strings protected by the same fuse. Required ampacity would then be 41 A.
The PV module conductors are only #12AWG (4mm2) and can only carry 20A per NEC 240.4(D)(7) (second problem)
But, in case of fault, the fuse will break because of other strings, therefore i cannot understand the article NEC 690.8(D).
Can i solve this problem with MC4 fuse connector #1 for each string (15A fuse) ? as defined in NEC 690.9 (E)?
Thank you in advance.
Paolo
- Modules power: 295Wp
- 19 modules for each string
- 2 strings in parallel (with ?Y? connector MC4)
- Short circuit current (Isc): 8.95A
Paolo