Is there any reason why one couldn't extend a pv stringer home run that was not long enough? So instead of a single continuous run from inverter to module a splice point with mc4 connectors would be used to make the run long enough.
 
Is there any reason why one couldn't extend a pv stringer home run that was not long enough? So instead of a single continuous run from inverter to module a splice point with mc4 connectors would be used to make the run long enough.

I don't understand what you are asking. What do you mean by "stringer"?

MC4 connectors are acceptable for use anywhere within the array, on a compatible size & type of wire.
 
Is there any reason why one couldn't extend a pv stringer home run that was not long enough? So instead of a single continuous run from inverter to module a splice point with mc4 connectors would be used to make the run long enough.
You can use MC4 connectors to extend any DC wiring you wish, provided that all other conductor considerations (ampacity, temperature, UV exposure, etc.) are observed.
 
Is there any reason why one couldn't extend a pv stringer home run that was not long enough? So instead of a single continuous run from inverter to module a splice point with mc4 connectors would be used to make the run long enough.

You can but it is not good practice.
 
While I agree it's not something to plan on doing, there's nothing wrong with doing it to fix a mistake.

I concur. I admit I have softened on this recently. The systems I have mostly been working on the last few years are ~400KW. Thats usually about 91 strings, and inevitably there is one or two that end up short. There are already 1428 pairs of MC4 connectors on the system, I think 4 more wont hurt anything :)
 
I concur. I admit I have softened on this recently. The systems I have mostly been working on the last few years are ~400KW. Thats usually about 91 strings, and inevitably there is one or two that end up short. There are already 1428 pairs of MC4 connectors on the system, I think 4 more wont hurt anything :)
True. While it is true that every connection/connector in a system is a potential point of failure, it is also true that when there are a bazillion connectors in a system, having a bazillion and one is not going to increase the chance of a failure by a detectable amount. Not only that, but every time a pair of modules in a string are not laid right next to each other in reach of the integrated cables, you have to add a jumper and therefore two more connectors. It's no big deal; just make sure that whomever is building your jumpers and home runs is proficient in making up MC4 connections and is using the proper tools.
 