dwils1980
Member
- Location
- Fort Collins Colorado
- Occupation
- Master Electrician, Building Inspector
I have an older meter main combo style service that is getting a PV system tied to it. This older meter main has a bussed connection on the load side of the meter going to the customer side of the equipment where you have 4 total slots. There is a 100amp breaker installed on the bus feeding the main panel leaving two slots open which will be used for a PV OCPD. To me this would qualify as a supply side connection, but article 705.11 only talks about sizing the PV system based on the size of service conductors. If the rating of the service equipment is 125 amps and the service conductors are 1/0 CU or larger that means I could potentially install a PV system sized larger than the max rating for the service bus. Any thoughts on this? Is there an article in the NEC that I’m missing that would prevent an installation like this?