I am working on a PV system with 5 inverters. Inverter output on units #1 , #2 is 29 amps each. Inverter output on units #3 , #4 , #5 is 9 amps each. Inverters feed a 125 amp sub panel, then feed a sub meter for homeowner use, then feed a outside fused disconnect, then a disconnect at main service area that is fed from the utility / line side of a 400 amp transfer switch. My question is do I need to have the disconnects rated at 125 amps or can I use 100 amps.
29 amps x 125% = 36.25 x 2 = 75.5 (2 - 40 amp 2p breakers in sub panel)
9 amps x 125% = 11.25 x 3 = 33.75 (3-15 amp 2p breakers in sub panel)
or can I use the inverter max. output only
29 x 2 = 58
9 x 3 = 27
85 amps