apu
- Springfield, NJ USA
It was more economical to contract out the solar install than reallocate my usual manpower or hire extra help to put the 125 panels on the roof and run all the wiring. And I'm happy with the workmanship. My only question is with the labeling they did. Am I misreading what the NEC (2014) requires?
On the two service disconnects (A & B in the attached drawing), they attached a label indicating that "terminals on both the line and load sides may be energized in the open position." That seems to be based on NEC 690.17(e) "Where all terminals of the disconnecting means may be energized in the open position, a warning label shall be mounted on or adjacent to the disconnecting means." Except, I don't see how this applies as the PV system line taps are ahead of the disconnect. If the load side is energized in the open position, there is a serious system fault that needs to be fixed. Just reading that label would lead me to believe it is a normal condition that doesn't need to be remedied.
They put that same label on the two main panels (C & D) (but not on the transfer switch or any of the five sub-panels). They also added "system is backfed" labels to both main panels and an "Inverter output connection. Do not relocate this overcurrent device" label on Panel C (but not D). But there is no PV connection to C or D (except via the line taps ahead of A & B) and no OCPD was added to Panel C.
I'm all for safety. And I'm okay with the more generic "solar electric system connected" and "turn off PV AC disconnect before working on this panel" labels downstream of the main disconnects. A "dual power source" label (not installed) would even be appropriate. But, from my reading of the NEC and just general common sense, I find these other labels misleading. Maybe they need them for their typical install, but they don't seem to apply here.
If I was coming in to work on the electrical system and wasn't here for the solar install, I'd be looking for what else I need to de-energize before working on the system instead of just throwing the disconnect, doing my job, and moving on with my day. And isn't the point of the labels to make sure anyone that comes in after I'm gone understands what they are looking at?
I'm reading 690.17(e) and 705.12(d); what am I missing?