Do I use the 90 degree chart or the 75 chart to begin derating of PV Wire? I am thinking specifically of application of the "number of current carrying conductors in a raceway" factor and the ambient temperature derate factor.
Does this change for THHN/THWN-2?
Assume the PV wire (or THWN-2) runs into inverter terminals. Are these terminals typically 75 or 90 degree rated?
Do i just stick to the good ole rule of "assume most terminals and boxes and switches etc are 75 degree rated, so just stick to the 75 degree chart for sizing the wire also, as it connects to it"?
Bonus: is cable tray a raceway, (wire mesh/snake tray) and would I apply a 50% derate for 20 PV wires in it?