T tdaug53 Member Nov 5, 2008 #1 Is the requirement for strapping 1" sch. 80 PVC every 3' the same as sch.40 PVC?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Nov 5, 2008 #2 Table 352.30 makes no distinction between different types of PVC conduit.
raider1 Senior Member Staff member Location Logan, Utah Nov 5, 2008 #3 I agree with Trevor, the rules in Article 352 applys to both schedule 40 and 80 rigid nonmetallic conduit PVC. Chris
I agree with Trevor, the rules in Article 352 applys to both schedule 40 and 80 rigid nonmetallic conduit PVC. Chris