Expansion fittings are generally provided in exposed runs of rigid nonmetallic conduit where (1) the run is long, (2) the run is subject to large temperature variations during or after installation, or (3) expansion and contraction measures are provided for the building or other structures. Rigid nonmetallic conduit exhibits a considerably greater change in length per degree change in temperature than do metal raceway systems.
In some parts of the United States and other countries, outdoor temperature variations of over 100?F are common. According to Table 352.44(A), a 100-ft run of PVC rigid nonmetallic conduit will change 4.06 in. in length if the temperature change is 100?F.
The normal expansion range of most larger sizes of rigid nonmetallic conduit expansion couplings is generally 6 in. Information concerning installation and application of this type of coupling may be obtained from manufacturers' instructions.
Expansion fittings are seldom used underground, where temperatures are relatively constant. If rigid nonmetallic conduit is buried or covered immediately, expansion and contraction are not considered a problem.