Pvc and rigid

Merry Christmas

mannyb

Senior Member
Location
Florida
Occupation
Electrician
Can rigid conduit be used mixed with PVC when you can't meet the depths needed for PVC. It's deep enough for rigid but to shallow for PVC..
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yes you can use both types of raceways in the same run but the RMC is required to be connected to an EGC unless it complies with 250.86Ex(3).
 

mannyb

Senior Member
Location
Florida
Occupation
Electrician
Yes you can use both types of raceways in the same run but the RMC is required to be connected to an EGC unless it complies with 250.86Ex(3).

In my situation I would say no. The issue is i can't reach depth and would need to install all rigid and not half rigid
 