Is schedule 40 PVC allowed to be ran on the bottom of floor joints in an unfinished portion of the basement? Fused conductors
Yes. If the basement is subject to temperature change resulting in expansion of more than 1/4", You will need expansion coupling(s). Also use straps that will allow movement of the conduit for expansion and contraction.Is schedule 40 PVC allowed to be ran on the bottom of floor joints in an unfinished portion of the basement? Fused conductors