PVC Conduit for Fire Pump Service Conductors

Status
Not open for further replies.

dnbob

Senior Member
Location
Rochester, MN
Can pvc be used to run from a utility power source underground and transition to rigid/IMC underground before the fire pump controller/disconnect? 695.6A
 

Gregg Harris

Senior Member
Location
Virginia
Occupation
Electrical,HVAC, Technical Trainer
Can pvc be used to run from a utility power source underground and transition to rigid/IMC underground before the fire pump controller/disconnect? 695.6A


Wire the same as service entrance conductors starting with230.6 and it will lead you to 230.32 and then to 230.43 for different wiring methods

Underground service conductors shall be protected against damage in accordance with 300.5. Service conductors entering a building or other structure shall be installed in accordance with 230.6 or protected by a raceway wiring method identified in 230.43.
 