Can you install pvc schedule 80 conduit indoors in a corrosive industial environment.
352.10 Uses Permitted. The use of PVC conduit shall be permitted in accordance with 352.10(A) through (H).Can you install pvc schedule 80 conduit indoors in a corrosive industial environment.
Renosteinke
If I understand your post correctly, I disagree with your train of thought.
Art 100 is definitions - definitions are not prescriptive.
Section 90.4 gives the Authority Having Jurisdiction (AHJ) some leeway in his/her decision to allow or disallow an installation - but that AHJ may need to be ready to defend that position in court, and better have a really good reason for his/her decision.
Also, I learned long ago that logic has very little place in the NEC.
*Are you stating that if EMT is permitted in a particular location/installation in the NEC, and we see damage to the installation, that it should not be permitted? (EMT is just an example I chose)
I agree to an extent. Not every case of a damaged raceway means it is normally subjected to physical abuse. In the traffic area of a warehouse - it likely is subject to abuse. In some area not normally subject to traffic - accidents still can happen.Let's use that EMT example. Let's say someone runs EMT along the wall of a warehouse. As far as the NEC section on EMT is concerned, you can run EMT in a warehouse, so it's a 'legal' install.
Now, let's add a twist. You're sent to fix some EMT in a warehouse, EMT that has been trashed by forklift traffic. I submit that EMT is no longer a 'legal' methon for that specific run.
Why? Because the conduit is required to protect the wires. We have proof that, in this case, EMT was not adequate. Since Article 110 requires raceways to provide mechanical protection, and EMT failed to do so, simply replacing the EMT with new EMT is not a compliant solution. IMO, you need another solution.
If you relocate the wire run, or provide additional protection to the run, you've met 110's requirement.
I don't know much about chrome plating, have seen a little of hot dip galvanizing. Your chemicals were likely prep chemicals for the plating process. If the plating would be hot like for the galvanizing PVC would not hold up to the temp in the dip area, but there likely is no chemical in that area either.I did some work in a factory that chrome plated the hardware for shelf racks in stores. There were automated lines where material was dipped in various vats of chemicals.
Everything metal in that place including the building steel was rotting away. There were runs of wire where the emt had disappeared long ago. The thhn/thwn wiring was fine and so was the copper wire. We went in and installed pvc.
I'm just glad I didn't have to work in that place full time like the employees did. What will that stuff do you your health over time?