Have any of you dealt with Varian Linear Accelerators? As with many X-ray/Radiology pieces of equipment, there is a 208V connection from a shunt-trip breaker to a power distribution unit and then several conduits from that location to the actual Linac and to the control room, etc.
Some conduits contain low voltage signal cables only but others contain the X-ray or 208V power conductors, all of which are provided by the Linac installer.
The owner is requesting that we use PVC conduit in the slab for all low voltage and 208V (480V in some rooms). Given that this is a patient care area and I have power coming from a critical branch transfer switch, I feel that Article 517 would require metal conduits for a redundant ground path and the fact that it is critical power.
However, the cables and conduits don't really bond to a junction box or even the Linac itself. They generally just terminate in a pit below the equipment.
Am I missing something or could PVC conduit be used for such installations? I know I haven't covered all bases here in my question but I've always specified GRS conduit for X-ray installations previously for these reasons. The Owner is now asking me if the conduit pathway isn't continuous anyway, why use metal conduit?
Thanks.
Some conduits contain low voltage signal cables only but others contain the X-ray or 208V power conductors, all of which are provided by the Linac installer.
The owner is requesting that we use PVC conduit in the slab for all low voltage and 208V (480V in some rooms). Given that this is a patient care area and I have power coming from a critical branch transfer switch, I feel that Article 517 would require metal conduits for a redundant ground path and the fact that it is critical power.
However, the cables and conduits don't really bond to a junction box or even the Linac itself. They generally just terminate in a pit below the equipment.
Am I missing something or could PVC conduit be used for such installations? I know I haven't covered all bases here in my question but I've always specified GRS conduit for X-ray installations previously for these reasons. The Owner is now asking me if the conduit pathway isn't continuous anyway, why use metal conduit?
Thanks.