C Chris1122 Member Location Florida Occupation Electrical Jul 12, 2023 #1 Can PVC conduit be used on the exterior of a commercial building? Does anyone know the NEC for this? Thanks.
Can PVC conduit be used on the exterior of a commercial building? Does anyone know the NEC for this? Thanks.
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Jul 12, 2023 #2 Barring any building code issues, yes. But why? PVC on the exterior of any building never looks good due the sags. Since you are an electrician would not EMT be an option?
Barring any building code issues, yes. But why? PVC on the exterior of any building never looks good due the sags. Since you are an electrician would not EMT be an option?
roger Moderator Staff member Location Fl Occupation Retired Electrician Jul 12, 2023 #3 Chris1122 said: Can PVC conduit be used on the exterior of a commercial building? Does anyone know the NEC for this? Thanks. Click to expand... Have you looked in chapter 3?
Chris1122 said: Can PVC conduit be used on the exterior of a commercial building? Does anyone know the NEC for this? Thanks. Click to expand... Have you looked in chapter 3?
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Jul 12, 2023 #4 Sorry is this vertical or horizontal? Up from below ground is very common