PVC Conduit

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
In Chapter 9, Table 4, there are four Tables listed for PVC Conduit, One is Sch 80, One is Type EB, One is Sch 40 & HDPE and One is Type A, Sch 40.
Which Table applies to the "standard" Sch 40 normally used in above ground installations ?
 
Actually this was a "pass along" question from an "lurker" and the person initiating it was using Table 4 since it was conductors of different sizes.
If I recall correctly, Type A PVC is listed for concrete encasement but I wanted to confirm before I answered him.
 
Great, I would like one million dollars and if you could not report it to the IRS or my family that would be outstanding. :cool:

I can take care of the 2nd part of that right now. Poof. Done! :D

Now that first part.... that's going to take some time. :lol:
 
In Chapter 9, Table 4, there are four Tables listed for PVC Conduit, One is Sch 80, One is Type EB, One is Sch 40 & HDPE and One is Type A, Sch 40.
Which Table applies to the "standard" Sch 40 normally used in above ground installations ?


Sch 40& HDPE---The applicable table is the one that states art. 352 and 353-Rigid PVC Schedule 40. No other table states sch 40
 