We have a project in the northeast where PVC conduits are rising out of the ground, secured to unistrut and then open conductors into a cable tray via a weatherhead. Contractor used regular strut clamps to secure the PVC. I said that they either needed to put an expansion fitting in before the first strap or use a clamp that will allow movement. This would be an equal to a B-Line B2417-4ZN https://www.eaton.com/us/en-us/skuPage.B2417-4ZN.html The engineer came back and said that an expansion fitting is not required because the conduit does not go to a fixed point. I disagread with that and said that the unistrut clamps were a fixed point. The engineer approved a methood that I still dont agre with. That is adding a nut on the inside of the strut clamp and tightening up the clamp so that it does not lock tight to the conduit. The probleum now is the strut clamp can slide side to side and will over time fail and just seems like a poor fix. I also don't know if this is an approved methood from the manufacturer. I was only able to find installation instructions for Caddy strut clamps and they state that you tighten the bolt and screw. There was no mention of using a double nut. just for reffrence Caddy clamps were not used. Looking for opinions.