PVC Duct Bank

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
if i have pvc conduits below grade that are stubbing up into the bottom of switchgear on grade would they transition to rgs or similar when stubbing into the gear. would imagine you cant stub up through grade slab and into gear with pvc. i know spec usually dictates but i was curious of others experience. thanks.
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
Do they let you do site visits to the jobs you bid?

A picture being worth a thousand words, a site visit and regular talks with foremen would be priceless in your situation.

To answer your question, stubbing up into gear with pvc is extremely common.
 

mstrlucky74

Senior Member
Location
NJ
Do they let you do site visits to the jobs you bid?

A picture being worth a thousand words, a site visit and regular talks with foremen would be priceless in your situation.

To answer your question, stubbing up into gear with pvc is extremely common.


Thanks thought one would never stub up into gear with PVC.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Because every spec I've read says no PVC within footprint of building...except this one.

You might be able to get some dispensation to stub UG PVC into floor mounted gear. maybe they would be more amenable to it if you agreed to use sch 80 where it pops up into the gear.

personally, unless it is a huge amount of money involved, I don't like asking for variations from the spec. I'd be inclined to just run the last few feet of conduit that goes into the gear as rigid.

most places though, there are conduits that come out of the floor and are exposed and I am not real thrilled with exposed and vulnerable PVC, even when it is in compliance with the code.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Even if you are permitted to use a PVC 90, you have to take a look at the pull to see if it will be likely that the pull rope will cut though the PVC at the 90 and result in damaged conductors. If it will be a short easy pull, not an issue, but it is an issue on long difficult pulls.
 

mstrlucky74

Senior Member
Location
NJ
Even if you are permitted to use a PVC 90, you have to take a look at the pull to see if it will be likely that the pull rope will cut though the PVC at the 90 and result in damaged conductors. If it will be a short easy pull, not an issue, but it is an issue on long difficult pulls.


Thanks a lot...
 

cdslotz

Senior Member
The title of this post states this is a duct bank......a duct bank would be encased in concrete.

Is there a spec section about duct banks? A lot of them require long radius elbows...sometimes GRC and sometimes wrapped
 