PVC/EMT raceways bonding

Status
Not open for further replies.

cgar548

New member
If you have a feeder running in PVC raceways with properly sized equipment conductor entering a metallic box and bonding to the box--then exiting with EMT raceway( no equipment ground wire) without concentric or eccentric knockouts and with properly seated compression fitting--do you need a ground bushing and jumper conductor bonded to the box?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Nothing further is required. The box is grounded via the EGC and the raceway is bonded through the EMT connector.
 