anthonysolino
Senior Member
- Location
- Port St.Lucie Florida
I have a straight of conduit between two fixed boxes, 25' long with a 60F temp change, my calculation is 5/8-7/8" I had a manufacture I called instructed me to install this fitting in the middle (which was done shortly after my conversation) despite only having to need ONE joint, then I was sent a PDF (after the conduit was ran) of a NEMA article instructing me to install this joint "close" to the box and securely fasten the barrel, which I did, utilized a 1" clip, the rest was 1/2" now I have to go cut this joint out and move it over close to one of the boxes, does any one have any thoughts? if it were to be left in the middle, would the other end simply come out? I would think so, but maybe there is something I am missing here.
thanks every one!
thanks every one!