In 40 years in the trade, I've never installed this long a run of PVC. Basically, I'm running along a fence @ 200' of 1" pvc with (3) #6 THHN conductors and (1) #10 ground to provide a 30amp/230v receptacle at the end of the run.
Article 352 requires thermal expansion fittings. This job is in the East Foothills of the Bay Area. I'm going to assume a temperature difference of 20-110 degree F (90 degrees), which translates to 3.65 inches of expansion per 100'. So it appears I'll need (2) expansion joints on this run of pipe.
My question is, if the pipe expands that much, how do you allow for the extra wire length required? Loops in j boxes? How do you assure the wire will travel properly and in the correct direction upon detraction?
Thanks for the help.