Are there any burial depth requirements for a 1" PVC raceway run underground and under a one family dwelling driveway? The PVC will have Verizon FiOS fiber optic cable in it.
Are there any burial depth requirements for a 1" PVC raceway run underground and under a one family dwelling driveway? The PVC will have Verizon FiOS fiber optic cable in it.
Are there any burial depth requirements for a 1" PVC raceway run underground and under a one family dwelling driveway? The PVC will have Verizon FiOS fiber optic cable in it.
Even if it was covered by the NEC, it would be covered by Article 800, and 300.5 is not referenced in 800.
For anything in Chapters 1-7 to apply to a Chapter 8 installation, the rule in those previous chapters my be specifically cited in the Chapter 8 Article.That was my thought as well but in a recent discussion with another sparky he told me that he thought that 300.5 did apply. When I look at that table I don't see anything that's applicable. As others have stated this is likely outside of the purview of the NEC anyway.
I would double check the conduit size.
From what I recall the minimum size for FIOS is 1-1/2.
Everything is pre-made.
Sorry I forgot that in Washington we have a state rule that the chapter 8 wiring has to comply with the burial depth requirements of Chapter 3For anything in Chapters 1-7 to apply to a Chapter 8 installation, the rule in those previous chapters my be specifically cited in the Chapter 8 Article.
There was a PI that would make Chapter 8 like 5-7 are now, that was accepted at the CMP meetings, but that is subject to the actual ballot results that will be published in early July.Sorry I forgot that in Washington we have a state rule that the chapter 8 wiring has to comply with the burial depth requirements of Chapter 3 ...
There was a PI that would make Chapter 8 like 5-7 are now, that was accepted at the CMP meetings, but that is subject to the actual ballot results that will be published in early July.