PVC runs in and out of metal J-Box with no splices just a pull point but what article says the metal box must be bonded to EGC? Can't find it right now.
All metal parts must be bonded. The box must be bonded when running plastic conduit. 250.110
All metal parts must be bonded. The box must be bonded when running plastic conduit. 250.110
Dennis, am I missing something in 250.110? I don't see it as saying all metal parts must be bonded. It requires metal parts of fixed electrical equipment likely to become energized to be connected to an EGC, and only under the conditions listed in 1-6.
Okay look at 250.86-- I am sure there are other sections.
Okay look at 250.86-- I am sure there are other sections.