scnkapc
Member
- Location
- Northern Kentucky
If PVC jacketed MC Cable is listed for sunlight, direct burial and for exposed work does it still need protection from physical damage where it emerges from earth?
330.12 Uses Not Permitted
Type MC cable shall not be used where exposed to the following destructive corrosive conditions, unless the metallic sheath is suitable for the conditions or is protected by material suitable for the conditions:
(1) Where subject to physical damage
(2) Direct burial in the earth
(3) In concrete
(4) Where subject to cinder fills, strong chlorides, caustic alkalis, or vapors of chlorine or of hydrochloric acids
If it emerges from earth in the middle of a grassy back yard secured to a 4x4 post to feed a GFI, wouldn't that be concidered to be subjected to physical damage by lawn equipment (i.e. weedeaters) and if so, should it be protected by a SCH 80 PVC sleeve?
330.12 Uses Not Permitted
Type MC cable shall not be used where exposed to the following destructive corrosive conditions, unless the metallic sheath is suitable for the conditions or is protected by material suitable for the conditions:
(1) Where subject to physical damage
(2) Direct burial in the earth
(3) In concrete
(4) Where subject to cinder fills, strong chlorides, caustic alkalis, or vapors of chlorine or of hydrochloric acids
If it emerges from earth in the middle of a grassy back yard secured to a 4x4 post to feed a GFI, wouldn't that be concidered to be subjected to physical damage by lawn equipment (i.e. weedeaters) and if so, should it be protected by a SCH 80 PVC sleeve?