pvc jacketed mc cable.

Status
Not open for further replies.

stew

Senior Member
can anyone tell me what the correct fitting is for use with this pvc coated 12/2 mc is. A cgb fitting with the proper bushing works fine and seals as it should and very effective but is not"listed for the purpose". thx
 
You need to use a fitting that is listed for use with PVC coated MC cable.

HERE is a link to a PDF document that shows a type of fitting that is listed for use with this type of MC cable.

Chris
 