Hello
My inspector informed me that PVC male adapters are not rated to thread into hubs.
The print specified PVC mast, where do I find this rating
None of these- PVC terminal adapters, EMT connectors and SE cable connectors are listed for use in hubs. So how is it that 90% of all services around here use one of those three wiring methods? You can thank Mark Ode from UL. He wrote an article not too long ago about how only IMC and RMC are code complaint in hubs. Seems like the guys who wrote the standard are to blame when you violate just about every residential service out there. :rant:
Here's the article, guess your EI read it.
http://www.ecmag.com/?articleID=11585&fa=article
FWIW I will give my opinion.
When it comes to water tightness the inside of the raceway is also considered a wet location. What difference does it make if you get an occasional drop of water through those threads when you may get a few tablespoons of condensation inside the raceway every night when conditions are right for it? This has been my opinion about the stupid raintight EMT fittings they came out with a few years ago. Before those I always used EMT fitting in Myers hubs. You know how many of these EMT fittings I have installed and come back to within 1 year and the gasket has deteriorated from sunlight and the fitting leaks more than the old standard compression fitting did? Not to mention you about have to take the fitting completely apart to successfully insert the raceway most of the time. Those things are a joke.
Next is the reliability of equipment grounding. If you turn the fitting in until it is wrench tight why should there be a bonding issue? How many times do we thread RMC or IMC into a fitting until it is tight and then have to back it off to get the right deflection of a bend? Whether acceptable or not it is done, and likely is not as good of a bond as an EMT fitting that is tight in the hub.
:thumbsup:FWIW I will give my opinion.
When it comes to water tightness the inside of the raceway is also considered a wet location. What difference does it make if you get an occasional drop of water through those threads when you may get a few tablespoons of condensation inside the raceway every night when conditions are right for it? This has been my opinion about the stupid raintight EMT fittings they came out with a few years ago. Before those I always used EMT fitting in Myers hubs. You know how many of these EMT fittings I have installed and come back to within 1 year and the gasket has deteriorated from sunlight and the fitting leaks more than the old standard compression fitting did? Not to mention you about have to take the fitting completely apart to successfully insert the raceway most of the time. Those things are a joke.
Next is the reliability of equipment grounding. If you turn the fitting in until it is wrench tight why should there be a bonding issue? How many times do we thread RMC or IMC into a fitting until it is tight and then have to back it off to get the right deflection of a bend? Whether acceptable or not it is done, and likely is not as good of a bond as an EMT fitting that is tight in the hub.
Hello
My inspector informed me that PVC male adapters are not rated to thread into hubs.
The print specified PVC mast, where do I find this rating
Next time, thread a close nipple into the hub, then thread a female PVC adapter onto the other end of the close nipple.My inspector informed me that PVC male adapters are not rated to thread into hubs.