C codequestion Banned Location MD, USA Jan 19, 2018 #1 General notes in drawing says conduit shall be schedule 40 PVC for work exposed to weather. Is their such a thing as PVC work exposed to weather? Outdoor or underground?
General notes in drawing says conduit shall be schedule 40 PVC for work exposed to weather. Is their such a thing as PVC work exposed to weather? Outdoor or underground?
jumper Senior Member Location 3 Hr 2 Min from Winged Horses Jan 19, 2018 #2 Outdoors. Many times above ground will be speced schedule 80. See 352.10(F).
roger Moderator Staff member Location Fl Occupation Retired Electrician Jan 19, 2018 #3 Derek posted your answer. Roger