PVC to RMC and back to PVC

Michele

Member
Location
Massachusetts
Occupation
Electrical Designer
Hello to the Forum.
An electrical contractor is installing underground ductbanks, that transition to above ground. A design drawing indicates to utilize RMC for the conduit sweeps. The intention of the note was to run Schedule 80 PVC horizontally and transition to RMC for the stub up to above grade.
The contractor transitioned all elbows to RMC, even the horizonal elbows in the ductbank.
The installation is straight-horizontal PVC to RMC horizontal elbows, to straight-horizontal PVC, to an RMC vertical stub up.
As we could correct the note to be more specific, the question is this: Is there a concern for pulling the cable from PVC to RMC, to PVC to RMC?
Some ductbanks are completed with concrete encasements. The un-poured ductbanks could be corrected if recommended.
Is there a concern for the cable pull to transition as mentioned, if the correct fittings are installed and do not create and exposed edge concern at the elbow fittings.
 

busman

Senior Member
Location
Northern Virginia
Occupation
Master Electrician / Electrical Engineer
Some types of pull rope will cut thru a PVC sweep in short order. From personal experience, you only do it once.

Take care that the internal diameter of the Sched 80 is beveled at each transition. Esp important when fill is at maximum and with smaller raceways.
If you burn thru PVC that is in concrete, would you even know? I've burned ONE elbow; lesson learned.

Mark
 

busman

Senior Member
Location
Northern Virginia
Occupation
Master Electrician / Electrical Engineer
Hello to the Forum.
An electrical contractor is installing underground ductbanks, that transition to above ground. A design drawing indicates to utilize RMC for the conduit sweeps. The intention of the note was to run Schedule 80 PVC horizontally and transition to RMC for the stub up to above grade.
The contractor transitioned all elbows to RMC, even the horizonal elbows in the ductbank.
The installation is straight-horizontal PVC to RMC horizontal elbows, to straight-horizontal PVC, to an RMC vertical stub up.
As we could correct the note to be more specific, the question is this: Is there a concern for pulling the cable from PVC to RMC, to PVC to RMC?
Some ductbanks are completed with concrete encasements. The un-poured ductbanks could be corrected if recommended.
Is there a concern for the cable pull to transition as mentioned, if the correct fittings are installed and do not create and exposed edge concern at the elbow fittings.
250.86 Exception 3 would allow this, as long as the horizontal elbows are in 2" of concrete.

Mark
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I agree with the others. The EC may be doing the horizontals for his own benefit regardless of specs.
 

Michele

Member
Location
Massachusetts
Occupation
Electrical Designer
Thank you all for the great responses. I recall the vertical sweeps should transition from PVC to RMC due to pulling concerns so it does make sense to have a large radius sweep as a horizonal elbow. As you mentioned, as long as there is not a concern with the difference in internal diameters. Thank you again for your assistance.
 