Carultch
Senior Member
- Location
- Massachusetts
PVC expands so much, that just a single 10 ft piece expands more than 1/4" in typical outdoor ambient temperature ranges.
When used underground, I've rarely seen expansion fittings installed in the long runs below grade. And I'd expect sand to clog the piston, rendering it ineffective. A handhole may allow some thermal expansion accommodation, but other than that, I don't see expansion accommodation installed underground in practice.
I'm aware that the temperature swing is typically a lot less underground, maybe 10F instead of 100F. However, if 10 ft requires expansion accomodation above ground, then you would expect that 100 ft would require expansion below ground.
So my question is, how do you (if at all) accommodate thermal expansion in underground PVC?
When used underground, I've rarely seen expansion fittings installed in the long runs below grade. And I'd expect sand to clog the piston, rendering it ineffective. A handhole may allow some thermal expansion accommodation, but other than that, I don't see expansion accommodation installed underground in practice.
I'm aware that the temperature swing is typically a lot less underground, maybe 10F instead of 100F. However, if 10 ft requires expansion accomodation above ground, then you would expect that 100 ft would require expansion below ground.
So my question is, how do you (if at all) accommodate thermal expansion in underground PVC?