here is a couple pics I took today of some pvc pipe ran above a suspended ceiling in an office tenant space being renivated, it is cutting diagnally across a tenant space that is doesnt serve to feed a panel in the tenant space next door, whoever installed it pulled 4/0 urd quad to feed a 200 amp 3phase panel and must have realizied that they forgot that they needed a ground wire, so they black taped and zip tied some #4 bare copper to the outside of it....
 
Last edited:
ultramegabob said:
Im still trying to figgure out how to post pictures without people having to click on the blue words...
click the little box that looks like a picture of a mountain. and insert the hyperlink to the picture and it will work
 
Pierre C Belarge said:
Bob
It is good to see so many starting to post pictures.

It is not good to see the EGC on the outside of the PVC.

its not good to see power from a differnt meter chasing through the inside of a tenant space either:mad:
 
Not the first time I've seen an install like that. EGC can be outside of pipe.. 300.3 (B) This install just shows off this installers PPP. Ugly Install

Rick
 
Last edited:
r_merc said:
Not the first time I've seen an install like that. EGC can be outside of pipe.. 300.3 (B) This install just shows off this installers PPP. Ugly Install

Rick

which portion of 300.3 B do you feel that this complies with ? ( I read through all the listed sections and exceptions and I can't seem to find one which allows this installation).
 
r_merc said:
Not the first time I've seen an install like that. EGC can be outside of pipe.. 300.3 (B) This install just shows off this installers PPP. Ugly Install

Rick
Thats not what 300.3(B) allows. The exception in 250.102(E) only allows this for 6 ft and less. With the EGC on the outside the circuit impedance is much higher on a ground fault.
 