PVfarmer
- Newport County, Rhode Island, USA
Grounding electrodes are primarily for surge and lightning protection and are of no use for faults. Grounded systems are required to have an adequate low impedance path for the fault current to return to the source.
I'm missing one part here.
Say a hot wire in an outlet melts, so there is now current flowing through the EGC from that outlet to the main ground bar, which is bonded with the neutral bar in the MSP.
The fault current then goes to the neutral of "the source", meaning the XO of the xfmr, and back to the breaker to trip it.
So...how does the fault become part of the "overall flow", yet somehow get back to the breaker? Does the neutral/fault current get "added to" the line current in the xfmr in order to cause the trip?
the fault current flows through the appliance ground wire to the service panel where it joins the neutral path, flowing through the main neutral back to the center-tap of the service transformer. It then becomes part of the overall flow, driven by the service transformer as the electrical "pump", which will produce a high enough fault current to trip the breaker.