You did mention that in the thread title. What is the model number of the CB?I forgot that yes it's a gcfi breaker with no nuetral screw.
I probably should look at thread titles, but often I don'tYou did mention that in the thread title. What is the model number of the CB?
"They stop at 50A, and they are only for 208Y120V systems.
Not permitted for any application where the NEC required GFCI protection."
Yes, we offer QO/QOB- GFI 3 pole breakers in amperages of 15, 20, 30, 40, and 50.
NOTE that this breaker does NOT have provision for a load neutral conductor and is for use on 208Y/120 VAC systems.
For 240VAC use EPD/EPE breakers. (30ma ground fault protection)"
Where in a 3 phase device will you be using the Neutral on a branch circuit?I do not get why there are no bigger 3ph gfcis with neutral, even in the external standalone type.
These didn't exist several month ago. The date on the posted marketing brochure is 11/23. I needed 3ph gfci but... .Siemens lists 3-pole GFCI breakers for 208V with a load neutral and ampere ratings of 15 20 25 30 35 40 45 50 60 70 80 90 100.
https://digitalcontentcenter.compas.siemens-info.com/SIE_DS_3PGFCI.pdf
I don't know what the pricing or availability would be.
Where in a 3 phase device will you be using the Neutral on a branch circuit?
To explain; the Neutral in a GFCI serves two purposes; to power the electronics inside of the breaker, and to monitor Neutral current on SINGLE PHASE loads, so that you have something to compare the line current flow against. Square D makes their GFCIs so that they power themselves from Line to Line, so they don't need the Neutral for that purpose. Then in a 3 phase branch circuit, there would be no need to monitor the Neutral to compare current flow, because if any line is going to ground, you can simply compare to either of the other two lines. This same issue by the way is true for Square D 2 pole GFCIs as well (if the load device is not using the Neutral), although most people just connect the Neutral anyway out of habit.